Part Number: DRV8803
Tool/software:
Hello,
I'm using the DRV8803 to control 4 proportional solenoid valves like in this application:
- VCLAMP is connected directly to VM without the Option Zener. VM = +12V
- IN1-4: 25kHz, adjustable Duty Cycle
Behavior: when I try to measure the voltage between the valve with a multimeter: at red and brown arrows (respectively), the voltage drop is not the same as it supposed to be corresponding to %duty cycle*VM:
The following is the actual measured voltage at corresponding duty cycle of input signal
- 10%: 0.5V
- 15%: 1V
- 20%: 1,6V
- 25%: 2,3V
- 30%: 2.9V
- 35%: 3.5
- 40%: 4,1V
- 45%: 4.7V
- 50%: 5.4V
- 60%: 6.6V
- 70%: 7.8V
- 80%: 9.1V
- 90%: 10.39V
Is this behaviour normal? Am I missing something?
My solenoid valve is rated at 12V@150mA each.
Thanks very much for your help.
Best,